I got an old champion generator that i use to run my welder sometimes and while back the 220 30 amp breaker popped and would not reset. I ordered a new one through champion and when i got it i noticed it said 30 amp and 13.5 trip amps.
The old one said 37.5 trip amps.
So now it will barely ru the old 220 stick welder on a low setting lime 20 to 30 amps which it ran it fine befor. Also my little 110 volt welder it wont run it on the 20 amp 110 out let or the 30 amp 110 outlet. I contacted them about it and told me it shouldnt matter.
I think its the wrong breaker. Whats your thoights.
Couple pics of breaker. I got original breaker pic bit not the one in it now. Found a pic of one like it though
Its a 6500watt continuous