Running hydro to shed

merc_man

merc_man
Local time
4:27 AM
User ID
933
Joined
Feb 24, 2016
Messages
4,952
Reaction score
21,578
Location
southern ontario
Country flag
I would like to run hydro to my shed someday, not anytime soon. Probly not this year. But was just wanting some opinions on best way to do so.
Now i just run a heavy extention cord and that dont produce enough amps to run my welders properly.
Just wanting some advise on best way to get propper power supply to shed.

Would i need a sub pannel?
What guage wire to run from house.
House is only a 100 amp service.
Lenth of wire from house to shed would probly be about 80 feet.

What amps should i be looking to get out ther to run the small 110 volt welders.
4a44f1074e97365698f9523b9a16eb26.jpg
2a3f2f302025158d10f00867a28c0815.jpg


Sent from my SM-J320W8 using Tapatalk
 

Bigmac

Mastermind Approved!
Local time
1:27 AM
User ID
5937
Joined
Apr 19, 2018
Messages
5,430
Reaction score
37,453
Location
Oregon
Country flag
You only need a 20 amp circuit, that is 12/2 with ground. But it depends on the distance and how much load the panel is at now. A 100 amp panel is pretty small, but for a dedicated circuit you could go a little overkill on the wire at 10/2 with ground, and that would help for a longer distance. A standard 15amp circuit won’t do it
 

Glock37

Pinnacle OPE Member
Local time
4:27 AM
User ID
356
Joined
Dec 31, 2015
Messages
1,657
Reaction score
6,745
Location
Monroeville Pa
Country flag
Sub panal run #2 in conduit to panel inshed with proper size breaker isolate neutral and grounds in shed panel


Sent from my iPhone using Tapatalk
 

chipper1

Here For The Long Haul!
Local time
4:27 AM
User ID
1463
Joined
Jun 25, 2016
Messages
6,272
Reaction score
23,568
Location
Grand Rapids Mi
Country flag
Pretty sure you can do an 80% sub off the main panel, not that you need that.
I'd do 220/240or whatever you call it if possible, a decent 220 welder is a lot smoother than a 120 if you happen to be able/decide to upgrade down the rd.
I have an extension cord out to my shed too, but once I build a barn I plan to have a much larger line running to that, right off the pole.
 

David Young

Safety First !!!!!!
Staff member
Local time
4:27 AM
User ID
434
Joined
Jan 7, 2016
Messages
2,258
Reaction score
9,622
Location
vt
Country flag
Any chance the shed would be closer to the meter than your house? You could put a breaker box under your meter. Run 10 2 ug with a 20 amp breaker.

You want cheap or very well done? The number 2 in conduit is the best but will cost more. Basically you are matching the house service.

10-2 ug can be direct buried and is probably going to be the cheapest way to go. It probably be enough to give suitable voltage at full current over that distance.
 

merc_man

merc_man
Local time
4:27 AM
User ID
933
Joined
Feb 24, 2016
Messages
4,952
Reaction score
21,578
Location
southern ontario
Country flag
The sheds further then the meter by about 80 feet.
Any chance the shed would be closer to the meter than your house? You could put a breaker box under your meter. Run 10 2 ug with a 20 amp breaker.

You want cheap or very well done? The number 2 in conduit is the best but will cost more. Basically you are matching the house service.

10-2 ug can be direct buried and is probably going to be the cheapest way to go. It probably be enough to give suitable voltage at full current over that distance.

Sent from my SM-J320W8 using Tapatalk
 