The easiest thing to do for three phase is either buy or built a rotary phase converter .It's relatively simple ,you can google it .I lost count of how many I've built for other people .
In my shop I have a 5HP converter .240 single in,480 3 phase out ,also transformed to 240 three phase with a single phase auto transformer to get approx 265 single which will fire 277 volt lighting .
If you build a converter right it will run with approx 92 percent efficiency rating .Which if compared to single phase motors about on a par or maybe even a little better .Properly built they will start up to the rating of the motor used to build the converter with a combined load of up to three times that amount providing the largest motor does not exceed the size of the converter . Nothing magical about it,it's just an induction generator in another form .
 

RD35

Super OPE Member
Local time
1:13 PM
User ID
2806
Joined
Mar 14, 2017
Messages
109
Reaction score
318
Location
Bloomington, IN
Just skimmed through these posts. I am a little concerned about all the "wild leg"/"high leg" discussion. Not sure this ever got totally cleared up. The most common type of shop 3-phase for small shops and for commercial buildings is a 120/208V "wye" connected system. This system gives you 3 phases that all measure 208V from leg to leg and all measure 120V to ground. There is no "high leg" on this system. The high leg is present on a 240V center-tap delta system that has a center tapped transformer for 120V. So you have three 240V transformers connected leg-to-leg and one of them is a standard center-tapped Single Phase transformer like the ones used for homes.
So, if you are wanting to run a 120/208V 3-phase 4-wire system in your shop (wye connected) then you will not have a high leg to worry about. As mentioned earlier, you need to consult a qualified electrician who can survey your needs and then contact the utility provider to determine what is available from them at your location.
Lastly, I would also recommend you check the rates that are charged for 3-phase power. It was mentioned in the opening post that 3-phase equipment pulls less amps. This is true....but it does not always pull less watts. The power company charges for wattage, not amperage. So by going to 3-phase your kilowatt-hour usage will not change (much anyway...maybe just a little less due to better efficiencies, but not much). So, the power usage rate ($/KW-H) is what I would look at as well as the minimum charges and install fees. Unless you are running a large shop with lots of 3-phase equipment, you may just want to consider a phase converter that creates 3-phase power from your single phase service like Al Smith suggested above.
Just food for thought. Hope this info is helpful.
 

paragonbuilder

Mastermind Approved!
Local time
4:43 AM
User ID
384
Joined
Jan 2, 2016
Messages
9,229
Reaction score
33,865
Location
Norwich, CT
Country flag
Just skimmed through these posts. I am a little concerned about all the "wild leg"/"high leg" discussion. Not sure this ever got totally cleared up. The most common type of shop 3-phase for small shops and for commercial buildings is a 120/208V "wye" connected system. This system gives you 3 phases that all measure 208V from leg to leg and all measure 120V to ground. There is no "high leg" on this system. The high leg is present on a 240V center-tap delta system that has a center tapped transformer for 120V. So you have three 240V transformers connected leg-to-leg and one of them is a standard center-tapped Single Phase transformer like the ones used for homes.
So, if you are wanting to run a 120/208V 3-phase 4-wire system in your shop (wye connected) then you will not have a high leg to worry about. As mentioned earlier, you need to consult a qualified electrician who can survey your needs and then contact the utility provider to determine what is available from them at your location.
Lastly, I would also recommend you check the rates that are charged for 3-phase power. It was mentioned in the opening post that 3-phase equipment pulls less amps. This is true....but it does not always pull less watts. The power company charges for wattage, not amperage. So by going to 3-phase your kilowatt-hour usage will not change (much anyway...maybe just a little less due to better efficiencies, but not much). So, the power usage rate ($/KW-H) is what I would look at as well as the minimum charges and install fees. Unless you are running a large shop with lots of 3-phase equipment, you may just want to consider a phase converter that creates 3-phase power from your single phase service like Al Smith suggested above.
Just food for thought. Hope this info is helpful.

Good post!
 

Blackgreyhounds

Super OPE Member
Local time
4:43 AM
User ID
1183
Joined
Apr 21, 2016
Messages
273
Reaction score
825
Location
S. Central PA
Country flag
Just skimmed through these posts. I am a little concerned about all the "wild leg"/"high leg" discussion. Not sure this ever got totally cleared up. The most common type of shop 3-phase for small shops and for commercial buildings is a 120/208V "wye" connected system. This system gives you 3 phases that all measure 208V from leg to leg and all measure 120V to ground. There is no "high leg" on this system. The high leg is present on a 240V center-tap delta system that has a center tapped transformer for 120V. So you have three 240V transformers connected leg-to-leg and one of them is a standard center-tapped Single Phase transformer like the ones used for homes.
So, if you are wanting to run a 120/208V 3-phase 4-wire system in your shop (wye connected) then you will not have a high leg to worry about. As mentioned earlier, you need to consult a qualified electrician who can survey your needs and then contact the utility provider to determine what is available from them at your location.
Lastly, I would also recommend you check the rates that are charged for 3-phase power. It was mentioned in the opening post that 3-phase equipment pulls less amps. This is true....but it does not always pull less watts. The power company charges for wattage, not amperage. So by going to 3-phase your kilowatt-hour usage will not change (much anyway...maybe just a little less due to better efficiencies, but not much). So, the power usage rate ($/KW-H) is what I would look at as well as the minimum charges and install fees. Unless you are running a large shop with lots of 3-phase equipment, you may just want to consider a phase converter that creates 3-phase power from your single phase service like Al Smith suggested above.
Just food for thought. Hope this info is helpful.
Good post!
FWIW, I have a home-brew rotary 3-phase converter to run an old jointer down in my woodworking shop. I bought it with the machine and had an electrician install it. Even though a converter is not perfectly ideal, it is very convenient to have the option of 3-phase service in addition to standard single-phase 120/240V when/if you are looking purchase used machinery. As @Al Smith said, for a small, home shop, it's definitely easiest and cheapest to buy/make a converter.
 

Leafy

Super OPE Member
Local time
4:43 AM
User ID
6062
Joined
May 3, 2018
Messages
356
Reaction score
647
Location
NH
Country flag
The easiest thing to do for three phase is either buy or built a rotary phase converter .It's relatively simple ,you can google it .I lost count of how many I've built for other people .
In my shop I have a 5HP converter .240 single in,480 3 phase out ,also transformed to 240 three phase with a single phase auto transformer to get approx 265 single which will fire 277 volt lighting .
If you build a converter right it will run with approx 92 percent efficiency rating .Which if compared to single phase motors about on a par or maybe even a little better .Properly built they will start up to the rating of the motor used to build the converter with a combined load of up to three times that amount providing the largest motor does not exceed the size of the converter . Nothing magical about it,it's just an induction generator in another form .

I wouldn't be so sure, last time I priced it out it was cheaper to buy a vfd than a rotary converter, at least in bridgeport and reasonable engine lathe sizes. The vfd are great if you are trying to run just 1 motor but they don't seem to like it when the load varies itself a lot, like if you tried to use it as the input power for a whole cnc. I'd like to get 3 phase at my next house but at least around here they won't wire it to residential zoned houses, need to find a house that's in a dual zoned residential and industrial or commercial.
 

Al Smith

Here For The Long Haul!
Local time
4:43 AM
User ID
537
Joined
Jan 14, 2016
Messages
6,117
Reaction score
13,512
Location
North western Ohio
Country flag
There's other options too depending on what you want to do .A static converter ,more or less just a start circuit for a 3 phase motor is rather cheap and is really easy to build .The short side is you only get about 60 percent of the power because one leg is missing but they work .Regarding CNC stuff ,you won't find many home shops where anybody has that stuff .I have however seen small commercial shops run them on a rotary converter .
I think way too many people take this stuff as if it were rocket science which it's not . However somebody like myself who knows it has a hard time explaining it .Counting my navy time I figure I've been doing this stuff for 51 years .My pension from the IBEW is based on 45 years of service which will start August 1 of this year .Time to pass the torch .
 

T.Roller

Mastermind Approved!
Local time
4:43 AM
User ID
1277
Joined
May 11, 2016
Messages
15,385
Reaction score
53,444
Location
Southeast, TN
There's other options too depending on what you want to do .A static converter ,more or less just a start circuit for a 3 phase motor is rather cheap and is really easy to build .The short side is you only get about 60 percent of the power because one leg is missing but they work .Regarding CNC stuff ,you won't find many home shops where anybody has that stuff .I have however seen small commercial shops run them on a rotary converter .
I think way too many people take this stuff as if it were rocket science which it's not . However somebody like myself who knows it has a hard time explaining it .Counting my navy time I figure I've been doing this stuff for 51 years .My pension from the IBEW is based on 45 years of service which will start August 1 of this year .Time to pass the torch .
Congrats on the retirement brother. IBEW local 175 here.
 

Al Smith

Here For The Long Haul!
Local time
4:43 AM
User ID
537
Joined
Jan 14, 2016
Messages
6,117
Reaction score
13,512
Location
North western Ohio
Country flag
IBEW #32 Lima Ohio ,about 19 years .Ford Lima Engine plant UAW #1219 28.9 years .
 

Fresch

Well-Known OPE Member
Local time
4:43 AM
User ID
5790
Joined
Apr 2, 2018
Messages
81
Reaction score
151
Location
Cny
I.B.E.W. lu#43 Syracuse N.Y. been retired one year, missed our $increase by 3 months . We have enough to make it to, past my death unless sword hits the fword.
 

Al Smith

Here For The Long Haul!
Local time
4:43 AM
User ID
537
Joined
Jan 14, 2016
Messages
6,117
Reaction score
13,512
Location
North western Ohio
Country flag
I think it might be note worthy to mention another one of my mad scientist stuff . I was given a 400 amp transformer DC welder .It was originally wired open delta mean using three phase through two transformers .I rewired it single phase and used a double Pi filter to remove the single phase ripple .I figured as it is it's about 200 amp which is plenty for what I do .It will run 5/32 " iron powder rods or 3/16" fast freeze rods like a 6010 which is plenty for what I do and is smooth as silk,very little if any ripple .
So stuff like this is not something taught in apprenticeship classes but never the less unconventional or not does work .
 

Junior Samples

Super OPE Member
Local time
4:43 AM
User ID
4982
Joined
Jan 6, 2018
Messages
276
Reaction score
733
Location
Richmond Ky
Just skimmed through these posts. I am a little concerned about all the "wild leg"/"high leg" discussion. Not sure this ever got totally cleared up. The most common type of shop 3-phase for small shops and for commercial buildings is a 120/208V "wye" connected system. This system gives you 3 phases that all measure 208V from leg to leg and all measure 120V to ground. There is no "high leg" on this system. The high leg is present on a 240V center-tap delta system that has a center tapped transformer for 120V. So you have three 240V transformers connected leg-to-leg and one of them is a standard center-tapped Single Phase transformer like the ones used for homes.
So, if you are wanting to run a 120/208V 3-phase 4-wire system in your shop (wye connected) then you will not have a high leg to worry about. As mentioned earlier, you need to consult a qualified electrician who can survey your needs and then contact the utility provider to determine what is available from them at your location.
Lastly, I would also recommend you check the rates that are charged for 3-phase power. It was mentioned in the opening post that 3-phase equipment pulls less amps. This is true....but it does not always pull less watts. The power company charges for wattage, not amperage. So by going to 3-phase your kilowatt-hour usage will not change (much anyway...maybe just a little less due to better efficiencies, but not much). So, the power usage rate ($/KW-H) is what I would look at as well as the minimum charges and install fees. Unless you are running a large shop with lots of 3-phase equipment, you may just want to consider a phase converter that creates 3-phase power from your single phase service like Al Smith suggested above.
Just food for thought. Hope this info is helpful.
I haven't worked in this for about twenty years but most utility companies were fazing out the Delta services and all going Y services for new construction. Lord I know there are alot of old services out there still.
 

Al Smith

Here For The Long Haul!
Local time
4:43 AM
User ID
537
Joined
Jan 14, 2016
Messages
6,117
Reaction score
13,512
Location
North western Ohio
Country flag
I've seen some really odd set ups .Try 480 delta corner ground. 480 delta through a "zig-Zag" transformer set up to get an impedance connected neutral for 277 volt lighting .
My 200 amp single phase service at my shop comes in at around 246-248 .Using a 240 to 24 volt transformer hooked as an auto transformer for boost I can get close to 270 which will fire 277 volt lighting .
 

Al Smith

Here For The Long Haul!
Local time
4:43 AM
User ID
537
Joined
Jan 14, 2016
Messages
6,117
Reaction score
13,512
Location
North western Ohio
Country flag
I could ramble on for hours about this stuff .However to the topic as I said before a rotary phase converter if built correctly has around a 92 percent power factor .This surpasses most single phase motors if converted to three phase .It's not magic ,just a simple application of physics that have been around since Ben Franklin flew his kite and shocked the pee out of his assistant .Ben had an ornery streak . Actually more than likely Tesla figured it out .He was smart enough not to fly a kite .
 

lljdavis

OPE Member
Local time
1:43 AM
User ID
1505
Joined
Jul 4, 2016
Messages
3
Reaction score
2
Location
Toledo, Oregon
Run a Kay Rotary phase converter to power my planer, sander and dust collector. Need to start the converter, then one machine at a time. It all works. All running off a 90a , 240v circuit.
 

Moparmyway

Its just a saw
GoldMember
Local time
4:43 AM
User ID
21
Joined
Dec 4, 2015
Messages
5,237
Reaction score
28,046
Location
In a meeting
Country flag
we have 13,800 stepped down to 4,160, which is distributed to the substations in our buildings. We use the 4160 for refrigeration machines and pumps to drive the motors. We have two transformers in each of our many substations for stepping down to 480 distribution branch circuits through the MCC’s.

Watts is what’s metered, by kw, so like @RD35 said, it doesn’t matter what voltage/amperage one settles on, power is measured in watts
 

Al Smith

Here For The Long Haul!
Local time
4:43 AM
User ID
537
Joined
Jan 14, 2016
Messages
6,117
Reaction score
13,512
Location
North western Ohio
Country flag
Where I retired from,Ford Lima engine plant it was bought at 138 thousand volts transformed down to 13,800 to the roof top sub stations .From there transformed down to 480 Y /277 or 120/240 single .It was billed in units of 10,000 KVA at primary voltage ,which came from two different transmission lines from two different power companies .
 

Homemade

Pinnacle OPE Member
Local time
4:43 AM
User ID
2986
Joined
Apr 8, 2017
Messages
1,106
Reaction score
2,699
Location
Wisconsin
Country flag
I’ll give an update on my plans. We plan on breaking ground in spring and I’ve decided not to do the three phase house thing.
Three phase lighting doesn’t excite me. LED bulbs are more efficient and common to source. Same goes with heating appliances.

When it comes to shop tools. I started leaning about VFDs and how then can take 220v single phase and turn it into 230v three phase for way cheaper than any savings I would gain. And putting a VFD on a lathe or mill, I also get rpm adjustment without sacrificing torque, jog function, and reversing is way easier.
 

blades

Super OPE Member
Local time
3:43 AM
User ID
7181
Joined
Aug 30, 2018
Messages
288
Reaction score
424
Location
Leroy, WI
Country flag
providing the motor is compatible with VFD.
 

Al Smith

Here For The Long Haul!
Local time
4:43 AM
User ID
537
Joined
Jan 14, 2016
Messages
6,117
Reaction score
13,512
Location
North western Ohio
Country flag
If memory serves those motors were classified as being compatable for "inverter" duty .You could probably find out on Google .VFD's are kind of neat ,single phase,rectify that and spit out variable frequency three phase .I've installed them,changed them but never did any repair on them .A box with a bunch of goobley gook with no theory of operation or wiring diagram making them kind of an OEM contraption .

At work when a unit failed I'd try to glean some info via the internet or sic a controls engineer on it .More times it just got changed out and the bones shipped off to the manufacture .
 
Top